7/25/2019 3:55 PM | |
Joined: 7/15/2011 Last visit: 5/12/2024 Posts: 48 Rating: (0) |
Hello, I am using PAC3200-7KM9300-0AE01-0AA0 and CPU 315-2PN. I have made the communication between PLC and PAC, but couldnt fetch the data as I required. Configuration and the logic as in attachment. But the value is 0. Request your help asap. ------------------------------------------------------------------------------------------ AttachmentDoc1.docx (198 Downloads) |
Last edited by: Jen_Moderator at: 07/26/2019 07:15:37New subject after splitting |
7/25/2019 4:12 PM | |
Joined: 12/18/2014 Last visit: 7/9/2024 Posts: 33318 Rating: (4130) |
Take a look at this this Siemens manual: SIMATIC Modbus/TCP Connection of Sentron PAC 3200/4200 to a SIMATIC PN-CPU |
7/25/2019 6:10 PM | |
Posts: 3093 Rating: (323) |
Hello, For Profinet, what you parameterized, you need an additional moldule for PAC3200. Delivery release: Switched Ethernet PROFINET Module For ModbusTCP you need an addtional library. Which of these possiblilities are you going to use? Regards, |
This contribution was helpful to1 thankful Users |