Import of a Technical Question of the User mrgh
|
6/11/2014 9:57 AM | |
Joined: 10/9/2007 Last visit: 10/8/2024 Posts: 1250 Rating: (115)
|
Hi /BB and /FF are hardware versions. Some old hardware don't accept newer firmwares. You can find information about them on Downloads/Firmware/Service Information in https://w3.siemens.com/smartgrid/global/de/produkte-systeme-loesungen/schutztechnik/transformatordifferentialschutz/Pages/7UT613.aspx# First the firmware must be compatible witth hardware, then the Parameter set must be compatible with firmware. P-Set 4.01.03 is quite old and firmwares 4.00.10 to 4.03.01 are compatible only with hardware up to EE. So you probably must update firmware and then use a newer parameter set. Updating parameter set in Digsi is not possible for older P-Set. You find this informaiton in the same link above, under Update Parameter set. Mike |
Energy Automation products: Sicam, Siprotec, Digsi |
|
7/27/2024 1:04 AM | |
Joined: 5/17/2024 Last visit: 8/5/2024 Posts: 1 Rating: (0) |
Hi Please I have siprotec 7UM6215-2EB92-3AA0+L0A. And hardware version FF and p Set version V4.70.02 I need to order spare of siprotec what is the data must be mention in the order and if found same hardware version and different in Pset it will be compatible or not Thanks for you.
|