11/17/2020 5:55 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, Please refer SIMOREG DC-MASTER 6RA70; software version 3.1 manual, chapter 7.5 Start up for setting drive motor commissioning parameters. In your case set P082 = 0, P083 = 3, conduct optomisation proceduers (p051 = 25 & p051 = 26) one by one, save parameters & run motor with drive. HTH |
Last edited by: Jen_Moderator at: 11/17/2020 08:22:44Optimized link. |
|
11/22/2020 2:17 PM | |
Posts: 3 Rating: (0) |
Yes, no load while doing P051-25 and the correct motorparameters are set. I will check the parameters you mentioned ASAP. I'm not in the area right now. Thanks! |