Please help me to understand the parameters required to connect a drive to plc and also the difference between cyclic and acyclic data exchange in profibus. ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 3/9/2017 9:55:33 AMNew subject after splitting |
|
3/9/2017 3:36 PM | |
Joined: 8/3/2009 Last visit: 9/27/2024 Posts: 13792 Rating: (1741) |
Hello and which Engineering Software?? Bye Murof |
If this Information really helps, you could use the Rate function |
|
3/10/2017 8:34 AM | |
Joined: 7/9/2015 Last visit: 9/27/2024 Posts: 3947 Rating: (587) |
Hi, first you need a GSD/GSDML File to project your Hardware in Step 7 / TIA. There you can choose your Telegram-type like Statusword etc. With instructions DPRD_DAT/DPWR_DAT you can exchange Data with PLC to / from drive. Check this example: How Can You Integrate a Drive into the TIA Portal via the Device Master File (GSD)?or https://support.industry.siemens.com/cs/de/en/view/109475963 Regards, Towome |
|
|