9/2/2019 5:18 PM | |
Joined: 5/3/2017 Last visit: 4/19/2024 Posts: 673 Rating: (216) |
Hello HAMAS121, in the manual S7-400 Automation System, CPU Specifications at section Cycle Time Calculation you can find the CPU times for process image updating. With regards |
9/3/2019 9:33 AM | |
Posts: 32 Rating: (2) |
Hello, can you give us a little detail about your order control system. knowing that the cycle time between a PLC and PLC is defferent Best regaurd |
9/4/2019 3:57 PM | |
Joined: 9/9/2015 Last visit: 5/10/2024 Posts: 727 Rating: (268) |
Dear HAMAS121, You can definitely integrate the 2 Omron PLC into PCS 7. In fact, you can expand the plant much more by using the Server/Client configuration. For a small system, you can refer to the standard architecture link I attached below for more information. Please read this Standard Architecture For the architecture shown in your drawing, I found something might cause a problem. I saw the ethernet connection and Profibus is 200m. My best practice is, the ethernet connection is less than 100m and for Profibus is less than 150m (1.5Mbps). Longer than that, please use fibre optic / Optical Link Module / Profibus Repeater. I attached the suggestion here as a picture. Hope it helps. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|