Joined: 10/6/2011 Last visit: 2/12/2024 Posts: 42 Rating: (3) |
from post https://www.automation.siemens.com/WW/forum/members/PostReply.aspx?PostID=439938&Quote=True&Language=en&onlyInternet=False
|
This contribution was helpful to3 thankful Users |
10/28/2014 5:44 PM | |
Posts: 1 Rating: (1) |
Another success story here! We had the same thing on a new install where for whatever reason there were connectivity issues (Windows 7 x64). Neither the Primary Setup Tool nor the Display Accessible Nodes tool would detect a freshly wiped CPU319F-3 using the ISO adapter protocol. Followed your directions to delete the adapter in the Windows Device Manager, deleted the associated XML files, reboot, and voila, PST and Display Accessible Nodes is able to see the CPU! Thanks for sharing this! |
Last edited by: DanoNH at: 10/28/2014 5:45 PM |
|
This contribution was helpful to1 thankful Users |
2/13/2018 9:59 AM | |
Joined: 11/25/2017 Last visit: 9/12/2024 Posts: 24 Rating: (0) |
Hi, How to solve same problem in windows xp. My PG/PC interfeace has similar problem. Regards Aiyub |
2/20/2018 3:33 PM | |
Joined: 8/3/2009 Last visit: 10/11/2024 Posts: 13911 Rating: (1757) |
Hello If you have Problems with PGPC Settings you can check this FAQ: http://support.automation.siemens.com/WW/view/en/11870489 Bye Murof |