10/29/2014 10:42 AM | |
Posts: 6 Rating: (0) |
Dear all I have the same problem with a Phoenix Contact EEM-MA400. My question is: where do you specify the offset? I have the adress50780. So if I want to access teh data 780 where do I specify the 50000 offset in the FB3? ( I am using ET200S modbus master module) ----------------------------------- New subject after splitting from Socomec E34 RTU slave device. |
Last edited by: Min_Moderator at: 10/29/2014 11:36 AMSplitted |
|
10/29/2014 5:36 PM | |
Posts: 3093 Rating: (323) |
Hello Just_Ioana, you define it in the source SEND_DB. Just have a look at section 3.5.7 of the 1SI manual. Regards, Kaulquappe |