Hi Murali.R, the problem is that the dead time between MV and PV is so big, that you have to consider it at the PID. Have you tried to use the a Smith Predictor? The Smith Predictor is a way to optimize the process control with big dead times. A normal PI controller must be tuned very sluggish for processes with large dead times and the control performance will decrease accordingly. The control performance can be considerably improved with the help of a so-called Smith-Predictor. With regards |