2/20/2019 7:38 PM | |
Posts: 14 Rating: (0) |
hellow, in attachment i send you the text file its happening every day around the same hour i intall the last firmware version AttachmentDiagnostics.txt (185 Downloads) |
2/20/2019 7:51 PM | |
Joined: 9/21/2012 Last visit: 9/23/2024 Posts: 4165 Rating: (464) |
You have a 8DI/8DO card that is losing communication to the PLC. |
3/9/2019 7:56 PM | |
Posts: 14 Rating: (0) |
i switch the power suply from 2.5A to 5A buth problem stay's i try to switch the 8di/do into 16di/do that i have here. maby problem is in the card? |
4/28/2019 9:23 AM | |
Posts: 14 Rating: (0) |
hellow i change the card a few mothns ago and i have no problems anymore |