7/4/2010 8:06 AM | |
Posts: 8 Rating: (0) |
Hello Daniel Chartier, AttachmentERROR message AB.zip (208 Downloads) |
7/4/2010 2:06 PM | |
Joined: 9/27/2006 Last visit: 7/14/2024 Posts: 12268 Rating: (2675) |
Hello RNK; Pleaseshow us the slave configuration details of the CPU 313C-2DP. The AB message says that the slave is not configured and not responding. The S7 meaasge seems to say that the 313C is set up as a master (it Says Number of distributed Stations = 0, which is a DP-Master error). You will find in the following link a standard setup of a S7-300 PLC as a slave to a different family of DP-master (an IM 308C, of the S5 family in this case). Use it as a basis to setup your 313C-2DP as a slave to your A_B master: http://support.automation.siemens.com/WW/view/en/6709721 Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
7/4/2010 2:53 PM | |
Posts: 8 Rating: (0) |
Hello dchartier, Once again i thank you for your reply. I attached my program backup for your reference. I verified the link. i think i didnt missed anything. Regards RNK Attachmentjindal_t.zip (186 Downloads) |