I guess he means I/O Module of MM440 Please look at attachment for how to remove it And also refer Manuals as you are new to drives, that will help you lot Operating Instructions: MICROMASTER 440 0,12 kW - 250 kW Parameter List: MICROMASTER 440 Regards, Devesh Vithani |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|
This contribution was helpful to1 thankful Users |
6/29/2012 10:33 AM | |
Posts: 6 Rating: (0) |
Thanks a lot mates!!! We could solve the problem. The problem was that a couple of pins of the I/O module were bend, so the external power supply didn't reach the CPU so comms fell down and so the red led was turned on. I attached the file I found in the Siemens webpage and helped me. I'm sure I couldn't have solved this without your help. You told me that the problem could probably be on the I/O module, and the "-----" told me that the problem could be in bended pins. And finally the problem was just the conbination Many thanks!!! AttachmentThe display on my BOP shows - - - - -. What could cause this.pdf (152 Downloads) |