6/25/2013 2:22 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (708) |
Hi SB1986M, you can send us your block, and do not use twice the same output. |
6/25/2013 2:29 PM | |
Posts: 559 Rating: (87) |
Dear SB1986M, What DS SURESH KUMAR said is exactly right. You can't use same output in the logic again & again for different conditions. Because as per PLC scan cycle, it always make actual result ON as per last output scan only. So if you have same situation then you can do one thing. You just make memory bits on for all the individual cases. Then make parallel contacts for all memory bits & final result of that parallel contact will be your actual output address. |
This contribution was helpful to1 thankful Users |