6/14/2010 2:50 AM | |
Joined: 1/14/2006 Last visit: 2/14/2022 Posts: 37 Rating:
|
I am facing simmilar problem when connecting this OMRON PRM21 to SiemensCPU315-2DP as slave.(6ES7 315-2AG10-0AB0). When I changed to use a DP_DP coupler (6ES7 158-0AD00...), every bit zero exchanged between the two masters was set to 1. Splitted from PROBLEM WITH ET200 PROFIBUS COMMUNICATION. |
Last edited by: O_Moderator at: 6/14/2010 11:46 AMnew subject after splitting |
|
6/14/2010 11:04 AM | |
Joined: 10/7/2005 Last visit: 9/28/2023 Posts: 2988 Rating:
|
Hello kk you say "every bit zero", but I wonder if you mean that only the first bit is ON every time. If so,please check the DIP switches of your DP/DP coupler and set the "DIA" (data validity indication) switch to OFF position (or do NOT use the first bit for user data). Have a look at chapter 4.2.2 of THIS manual for more on this subject. I hope this helps |
Cheers |
|
6/14/2010 2:05 PM | |
Joined: 1/14/2006 Last visit: 2/14/2022 Posts: 37 Rating:
|
Thank you, fritz. In fact we have all the bit zero of each byte exchanged set to one. I am going to check the Diagnose switch. In here I attached a few screen captures. For the PRM21 with CPU315-2DP as slave case, we had tried a set up with one CPU315 as master an the other as slave. The result is positive. It is the PRM21 with CPU315 that gave negative result. Regards, kk AttachmentDP-DP_PRM21_ config.zip (242 Downloads) |