6/3/2013 7:26 AM | |
Posts: 12 Rating: (0) |
But when I trying to connect to the drives I recieve this message |
6/3/2013 7:33 AM | |
Posts: 12 Rating: (0) |
And this is my test project created on ES with installed Starter |
6/3/2013 12:55 PM | |
Joined: 5/12/2006 Last visit: 11/18/2024 Posts: 22453 Rating: (3030) |
Hello, in your configuration you will use routing to the drives. Your PC is connected via Ethernet to the CPU an from the CPU to the drives via Profibus. For this configuration you must assign a PG/PC in Netpro to the CPU which is connected to the PC. More informations here: http://support.automation.siemens.com/WW/view/en/22794082 Regards Christoph |
This contribution was helpful to2 thankful Users |