Good day. Have a problem with download project to PLC s7-1214: "Modules with active test and commisiioning function can prevent the download process". |
5/17/2016 9:03 AM | |
Posts: 1529 Rating: (202) |
Means you probably are monitoring a program block or have something else online. |
5/17/2016 4:53 PM | |
Posts: 4 Rating: (0) |
In PLC were Force Values from previous project. Problem solved by erasing FV |