Hi, it is not problem of WinCC V7. Only you use the S5 definition in your old project. It is necessary to create s7chn.ini file in folder WinCC\bin and into file write following entries [Channel] S7String=0 see https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&objId=22014014&load=treecontent&lang=en&siteid=cseus&aktprim=0&objaction=csview&extranet=standard&viewreg=WW Best regards Jaromir |
Jaromir Hladik |
|
This contribution was helpful to2 thankful Users |
5/11/2011 12:44 PM | |
Posts: 8 Rating: (0) |
Thanks a lot Jaromir. Now the tags work properly |
2/13/2012 7:42 PM | |
Posts: 8 Rating: (0) |
Hello!! I have the same problem, and I already tried to create the .ini file like the link display but it doesn't work what could be the problem?? Thank you |
3/14/2012 4:47 AM | |
Posts: 8 Rating: (0) |
I already tried to create the file and to save in Program File\Siemens\Wincc\bin and the file is here, I don't know what more I made wrong? |
3/14/2012 5:19 AM | |
Posts: 1064 Rating: (72) |
change the tcp/ip to channel in the ini file liker the instructions ays and try it |
Last edited by: playerslight at: 3/14/2012 5:20 AM |
|
3/14/2012 5:12 PM | |
Posts: 8 Rating: (0) |
Thank you it work ok |
10/27/2015 10:34 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
New question published by lorenzo80 is split to a separate thread with the subject Wincc 7.3, avoid array of char for every code or description. Best regards |
6/21/2016 2:44 PM | |
Posts: 1 Rating: (0) |
i have same problem but with wincc v7.3 , but i cant create s7chn.ini file and soluton from siemens to read not to write :( |