Dear All, I Need ur help, my PLC siemens S7-300 have problem, led BF2 (blink) and SF (always on). I want to know, what is root cause of this. please help me. |
12/6/2016 9:43 AM | |
Joined: 5/12/2006 Last visit: 10/2/2024 Posts: 22388 Rating: (3015) |
Hello, 1.) open the Diagnostic Buffer of the PLC and show which error exactly is logged! With this error informations you can locate the device which is affected. It can be a adress problem if you change a device with a newer one and set the wrong bus Adress. Have you change anything on the machine before the BF/SF is goring red? The termination must be ON at the first and the last device on the PROFIBUS line. http://www.profibus.felser.ch/en/index.html?busabschluss.htm http://www.profibus.felser.ch/en/index.html?der_busabschluss_fuer_rs485.htm Regards Christoph |