11/17/2022 8:13 AM | |
Joined: 1/21/2013 Last visit: 7/26/2024 Posts: 3022 Rating:
Hi Hajakz, according to the Operating Instructions Proline Promag P 500 PROFINET, page 103 you have to split the value. The first two bits are showing the diagnostic information number, the next byte is showing the status and the last byte will always be zero. Written as hexadecimal value your given value is 0x034A0000. So the diagnostic information number is 0x034A (842), the status is 0x00 (No device error is present). Diagnostic information number 842 means Process limit (page 203). Kind regards AttachmentBA01724DEN_0520.pdf (165 Downloads) |
This contribution was helpful to
1 thankful Users |
11/17/2022 12:42 PM | |
Joined: 3/26/2018 Last visit: 6/26/2024 Posts: 53 Rating:
Follow us on