3/21/2012 8:10 PM | |
Posts: 5 Rating: (2) |
I just spent the last two days fighting this issue and succeeded, I think. A couple of big differences between V10.5 and V11 are that the system created DBs are now separated in System Blocks folder underProgram Blocks, which is nice. The other obvious, annoying and not taken care of by the conversion process is that Timer and Counter .parameter names have been changed (for the better but again not handled in conversion) - .CV = .COUNT_VALUE; .QU = Q_UP;... etc. The way I imported was to save all my OBs and DBs (excluding system created) into a separate library files in 10.5 the opening and loading the library files into V11.The library is converted as it is loaded.If the library conversion failed then I went back into 10.5 to drop some off.Obvious DBs to drop are for timers and counters, these will be regenerated later. Once you have your OBs and DBs convertedin the V11 library then you can drop them into a new V11 project. I would suggest dropping in the DBs first then the OBs (and FBs) that way you will probably avoid DB number duplication - I found this out the hard way. Then you go through all the networks with a red X and fix the dangling DB references one at a time. Thanks to Banginis123for the Library hint - Watchtables were the least of my problems but thanks anyway. |
This contribution was helpful to1 thankful Users |
11/3/2012 7:57 AM | |
Posts: 7 Rating: (0) |
I am also facing the same problem while opening the project of TIA portal v10.5 in TIA Portal v11 All suggetions are Wel-come Best regards, SANDEEP |