1/19/2013 2:54 PM | |
Joined: 9/8/2009 Last visit: 7/17/2023 Posts: 1410 Rating:
At each incoming pulse you add a value (data from instument like 1m3/pulse)to a totalizer value. |
1/19/2013 8:29 PM | |
Joined: 8/1/2012 Last visit: 7/31/2024 Posts: 179 Rating:
hello sarana6 I think you should specify your type of counting.there are twomode for HSC:frequency and count and this depends on your project situation ((see your private message)) |
6/24/2014 1:01 PM | |
Posts: 37 Rating:
if you have flow sensor which is giving you pulse. (Like GF+ 3-2536-P0). In this case you need 1- know the K-Factor as per the pipe size 2- enbale HSC counter 3-See the attch program snap shoot i am getting reading in m3/hr Whereas ID1000 will get the reading from the physical address of PLC (i0.0) Put the value of K-factor in calculator block.
Attachmentk_factor.pdf (1086 Downloads) |
6/24/2014 1:02 PM | |
Posts: 37 Rating:
program screen shoot is attah |
