6/20/2013 6:28 AM | |
Posts: 319 Rating: (9) |
Dear Experts, Can anyone elaborate the differences between PZD and PKW telegrams used in Drive Communication ? With regards, nand gate.
|
6/20/2013 3:56 PM | |
Joined: 10/11/2006 Last visit: 5/22/2024 Posts: 5849 Rating: (793)
|
Hello, insome fewwords PZD is sending and readingthe data continuos, needed for operation of a drive viea field bus communication. This happens cyclic. E.g.: from PLC to drive power on / of, speed setpoint, or from drive to PLC actual speed, actual current statu sword. PKW is used acyclic data communication (lets say on demand), for example reading the actual fault code or writing a parameter with an other value. The following description is a little bit older, but it gives a good set up: http://support.automation.siemens.com/WW/view/de/30566350 |
Last edited by: TechTeam at: 1/23/2014 10:00 AMWith best regards, |
|
This contribution was helpful to1 thankful Users |
6/20/2013 7:07 PM | |
Joined: 9/27/2006 Last visit: 5/22/2024 Posts: 12257 Rating: (2668) |
Hello nandgate; Chapter 3 of the following manual explains quite well the difference in the data areas PKW (parameter value) and PZD (process data) when communicating with a Micromaster MM4 drive: Operating Instructions: MICROMASTER PROFIBUS Optional Board |
This contribution was helpful to1 thankful Users |
1/23/2014 8:27 PM | |
Posts: 340 Rating: (6) |
new question is splittet to profibus communication, G120. |