9/12/2018 6:13 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Please check below parameter values. P50067, P50076, p50078[0], [1], P50082, |
9/12/2018 6:30 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Since your drive is not controlling field, please set p50078[1] = 0 & check. |
9/12/2018 6:35 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
What fault message pops up & at which optimisation processes? |
9/12/2018 8:32 AM | |
Joined: 4/28/2015 Last visit: 4/12/2024 Posts: 112 Rating: (3) |
There is no external field for this motor . Motor Data : Voltage :48V DC Current :128A Watts: 5000W Rpm :1360 I have attached the site motor connections as attached from the supplier. And currently at site the DC motor is only supplied with the Armature supply with no field. p50100 = 128; p50101=48; p50102=0; p50104=5000; p50105=0.1; p50106=5000; p50107=0.1; p50108=5000; p50109=0 ; p50114=600 Attachmentpics.zip (182 Downloads) |
Last edited by: Satheesh290692 at: 9/12/2018 8:36:31 AMThanks |
|
9/12/2018 10:50 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, From the attached drawing & motor details, the DC motor is series wound type DC motor i.e. its armature & field windings are connected in series as such user cannot directly configured the standard DCM, it needs to select 6RA80..-..S22 type DCM. Please refer Operating series-wound or compound-wound motor FAQ for better understanding. |
Last edited by: Jen_Moderator at: 9/12/2018 1:21:38 PMOptimized link. |
|
This contribution was helpful to1 thankful Users |
9/12/2018 11:28 AM | |
Joined: 4/28/2015 Last visit: 4/12/2024 Posts: 112 Rating: (3) |
Hi, Is there any possibility that a normal DCM can be converted to a S22 type DCM .
|
Thanks |
|