Hello Anshul_Tiwari; With PCS 7 (which does not support the S7-1500 R/H CPUs) you can setup ET 200SP HA modules in a redundant I/O configuration. You cannot configure redundant ET 200SP or ET 200MP I/O with a S7-1500 R/H system. Refer to the following documentation: SIMATIC PCS 7 High Availability Process Control Systems (V9.0 SP1) https://support.industry.siemens.com/cs/us/en/view/109754977 SIMATIC S7-1500 S7-1500R/H redundant system https://support.industry.siemens.com/cs/us/en/view/109754833 In the last manual you will find various examples of redundant architectures for the S7-1500 R/H system. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 06/04/2019 14:40:42Last edited by: dchartier at: 06/04/2019 17:10:03 |
|
This contribution was helpful to
1 thankful Users |
6/6/2019 8:03 AM | |
Joined: 7/13/2007 Last visit: 2/23/2023 Posts: 32 Rating:
|
Thanks Daniel for such exact clarification. |