10/13/2010 7:49 AM | |
Joined: 10/7/2005 Last visit: 5/24/2024 Posts: 3007 Rating: (1049)
|
Hello Pranish's you are correct, you can have a maximum of 2 (two) F-Runtime groups (aka F-Call's). Most Safety applications tendto get by with using onlyonly one F-Runtime group, if you do need a second one though please make sure to check out the most important rules below (taken straight from the Distributed Safety - configuring and programming manual which has more on this) • The channels of an F-I/O can only be accessed from one F-run-time group. • A DB for run-time group communication can be read- and write-accessed by the F-runtime group for which you furnished the DB, but only read-accessed by the "receiver" F-runtime group. • The F-communication DB can only be accessed from one F-run-time group. |
Cheers |
|
This contribution was helpful to2 thankful Users |
10/13/2010 7:53 AM | |
Joined: 3/24/2009 Last visit: 6/20/2023 Posts: 535 Rating: (112) |
Dear Pranish's, as you said, Distributed Safety allows max. 2 F-Runtime-groups. There is no way to change this limit - sorry.
Best regards, yy1 |