7/5/2013 11:39 AM | |
Posts: 95 Rating:
Hi I want to change damaged analog input (ET200) on s7 400 during plc running. how can I do that? |
7/5/2013 12:43 PM | |
Joined: 9/27/2006 Last visit: 7/31/2024 Posts: 12272 Rating:
Hello muffi; What family of ET 200_ are you planning to modify? ET 200M, ET 200S... If you do not know, give us the part number of the head module of your remote IO station. What you are trying to do is called CiR (configuration in run). Here is some information on the subject: Planning expansion with ET200S (Best solution: CiR, Option Handling, spare modules)??? What should you watch out for when adding components or changing their parameters using CiR (Configuration in Run)? |
7/5/2013 1:13 PM | |
Joined: 3/18/2008 Last visit: 12/8/2023 Posts: 1750 Rating:
Hello, Have a look at this thread |
VANDE MATARAM..... |
7/5/2013 3:58 PM | |
Joined: 1/21/2013 Last visit: 6/6/2024 Posts: 4620 Rating:
Hi muffi, If you have the modules in operation CiR you can do it! |
7/5/2013 4:41 PM | |
Posts: 95 Rating:
thank dchartier the hardware is ET200M |
7/5/2013 4:51 PM | |
Hi muffi, Please give us the order numbers of the units. Which DP slaves can be added to and removed from a PROFIBUS ... |
2 thankful Users |
7/5/2013 5:38 PM | |
Posts: 95 Rating:
order number: 6ES7153-2BA00-0XB0 |
7/6/2013 9:54 AM | |
Hi muffi,
7/7/2013 8:48 PM | |
Posts: 95 Rating:
hi actually i want to now the risk of stop PLC |