Hallo Edy C, no, this is not possible. The analog / digital converter of an analogue input of the LOGO! converts the signal into 1000 units. For a 4-20 mA signal this results in: For the 4-20 mA signal, if the sensor type is 4-20 mA, the first 200 units will be hidden so that only 800 units will be available for the program, namely units 201 - 1000.