9/26/2013 3:52 PM | |
Joined: 1/9/2013 Last visit: 10/29/2024 Posts: 46 Rating: (21) |
Dear Gabriele Corrieri Synco 200 is simple to configure, as attachment a guide for commissioning without PC. This guide will help you to understand how it work's. There is also a basic documentation for the Synco 200 controller (to big to send in this forum), you certainly will find as dowload in the internet, if not let me know, we'll find a solution. Best regards Richard AttachmentSynco_200_Commissioning_guide.zip (1175 Downloads) |
Last edited by: O_Moderator at: 9/27/2013 7:48 AMattachment reattached |
|
10/4/2013 7:42 AM | |
Joined: 1/9/2013 Last visit: 10/29/2024 Posts: 46 Rating: (21) |
Hello Gabriele RLU arenice controller and simplyto configure if you know how it works;-) If you have a 3p actuator then you have to go in the commissioning menu and in the CONFIG, choose the CTLOOP1 and in the output S4 select 3P and in the same menuCONFIG go to 3P, in thisparameter set yes instate no and the output Q1 and Q2 will be configured as 3P command.In the setting of this3Pyou have to set thepositioning time (125s). But you don't have anymore acommand for the pump. As attachment the basic documentation of theRLU controller. Hope this will help. Best regards Richard AttachmentC:\Users\chafrri0\Desktop\Basic Documentation_Universal Controllers RLU2.pdf (1074 Downloads) |
This contribution was helpful to1 thankful Users |
Follow us on