11/14/2014 9:29 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
|
Hello, Check your connections again, make sure you have bridged 1 off the compensation terminals and have put the one compensation lead to the right terminal. see attached PDF for the right connections and bridging. Edit: I see page 401 is corrupted, please download complete Module data manual here Regards, Marcjan Attachment6ES7 331-7PF01-0AB0_con.pdf (101 Downloads) |
Last edited by: Marcjan at: 11/14/2014 9:44 AMProblem solved? |
|
11/14/2014 3:07 PM | |
Posts: 209 Rating: (2) |
Hi marcjan, I have checked all the connections and it is correct. If I short the terminals that was indicated in the manual would it solve the problem??or would the eratic signal still persist?? RTD don't have a ground connection a ground connection right?? Thanks for the response regards, raffy
|