3/29/2020 1:35 PM | |
Posts: 95 Rating:
Hi LOGO! Fans, I have created a UDF that I have used successfully on a few projects and thought I would share it here should others benefit from it. I created it for the LOGO! 8.FS4. It records the run time, total time and total run counts for the attached logic (motor, pump, heater etc.) It saves a lot of redundant programming if there are several pieces of equipment that need to be recorded. Two inputs – Run and Reset. The output is parameters that can be used in various other logic tasks and for screen data. Please let me know if you find it useful! Cheers, Darren AttachmentRunTime UDF.zip (748 Downloads) |
This contribution was helpful to
5 thankful Users |
3/29/2020 1:53 PM | |
Posts: 95 Rating:
Attached is an quick example of the Run Time UDF used for a screen display on a LOGO! Cheers, Darren AttachmentRun Time UDF Example.zip (720 Downloads) |
1 thankful Users |
1/3/2022 7:45 PM | |
Joined: 12/18/2014 Last visit: 7/15/2024 Posts: 33348 Rating:
In the example LSC are the values shown in the LOGO! display. |
4/19/2023 6:30 PM | |
Joined: 9/14/2022 Last visit: 6/4/2024 Posts: 1 Rating:
Looks like you can view them but they're not editable |