8/8/2019 4:47 PM | |
Joined: 3/9/2012 Last visit: 5/16/2024 Posts: 95 Rating: (8) |
Hello, with ALM I know you can use MASTER / SLAVE configuration. For example one CU with 4 ALM in parallel on one transformator and up to 4 on the other (with another CU with communication). You can check the following manual: https://support.industry.siemens.com/cs/ww/en/view/83180185 Zako |
8/9/2019 12:10 PM | |
Joined: 4/2/2016 Last visit: 7/13/2022 Posts: 413 Rating: (6) |
unfortunately I do not plan to use ALM, I will use only SLM... according to SINAMICS - Low Voltage Engineering Manual 2017 (en)... I can not understand the sentence With 12-pulse parallel connections, up to four Smart Line Modules are supplied by a three-winding transformer on the line side. In this case, an even number of modules, i.e. two or four, must be divided between the two secondary windings. could you explain to meup to four SML This is for one transformer winding or for both? even number 2 or 4, an even amount of everything on all the windings? Can i use configuration in 12-pulse par. connections #1 can i use configuration CU320-2 + 3 x SLM + CU320-2 + 3 x SLM (it's not an even amount?)? #2 can i use configuration CU320-2 + 4 x SLM + CU320-2 + 4 x SLM ? |
Last edited by: _oleksandr_ at: 08/09/2019 12:42:55 |
|