Hi, The CPU S5-102U is a bit of a special one... ACPU 102 has 2 different modes: "Test Mode" and "Normal Mode" Probably the CPU is now in "Test Mode" which is much slower but leaves more possiblities for monitoring/debugging. It's all decribed very well in the manual which you can find here: http://support.automation.siemens.com/WW/view/en/1091978 Read Chapter 4 and also See page 7-21 for more understanding
1. Reset the PLC 2. Turn off the PLC 3. Plug in memory submodule 4. Turn on the PLC - Red LED flickers when program loaded |