[quote user="ILYAZ"]I have CP 1430 with my S5 CPU. Can i connect it with S7 network directly.? Is there any special software or hardware settings involved.? I also heard that S5-S7 communication in this way is not reliable and compatibal.The link usally breaks frequently.Have You tried it yourself. Hi Ilyaz, It is depending from your hardware, the newest CP 1430 have a AUI- and a ITP-port on the same D15-plug. Older ones only have a AUI interface and need a converter to get it work for example with the Scalance X101 AUI. If you have the newest one {6GK1143-0T....} then you have to buy a crosscable with on one side a DB15 connector and on the other side a RJ45 plug {6XV1850-2SE50 TP XP Cord 15/RJ45 0.5 m, seeFAQ http://support.automation.siemens.com/WW/view/en/4557639}. This cable can directly be placed on a Scalance X0005, X100, X200 or X400 series switch. The CP 1430 is working with Half Duplex and only 10Mbit/S. Between S5 and S7 is the communication very reliable, but there must be the right equipment between the two systems. One thing where must be taken care off is that a S7-connection have always 2 connections (SEND and RECV) on one TSAP, for S5 is this normal 1 connection a TSAP, but you can also give 2 connections on 1 TSAP. See the FAQ ISO Transport Connection between the SIMATIC S5 and SIMATIC S7 via Industrial Ethernet And also when you have a CP 1430 TCP the FAQ TCP connection between S5 and S7 on the S5 side |
Last edited by: Late at: 12/31/2006 7:23 PMI hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|