5/24/2021 1:35 PM | |
Joined: 6/19/2019 Last visit: 10/29/2024 Posts: 705 Rating: (76) |
Hello, I think it will work. |
5/24/2021 1:40 PM | |
Joined: 9/27/2006 Last visit: 11/7/2024 Posts: 12293 Rating: (2691) |
Hello Poljo; The S7-1200 expansion cable you are pointing to is designed to connect a CPU to a SM (DI, DO, AI, AO module) at a distance of 2 m, but not to a CM See te S7-1200 Programmable Controller manual for details on the insstallation of this cable: https://support.industry.siemens.com/cs/ww/en/view/109797241/139335322123 However, since the CM can be installed on the left of the CPU O_Einstein has a suggestion in this discussion that could help you, refer to his last reply: Hope this helps, Daniel Chartier: |
Last edited by: dchartier at: 05/24/2021 13:42:41 |
|
Follow us on