8/4/2011 11:58 PM | |
Posts: 5 Rating:
|
Works great for me..... i'll try to upload the project tomorrow, i don't have it here. |
8/5/2011 1:02 PM | |
Posts: 126 Rating:
|
I started a new thread specifically for Modbus TCP on V11 SP1. /tf/WW/en/Posts/61602#303163 |
12/4/2013 4:17 PM | |
Posts: 46 Rating:
|
Dear Sirs, I have used anapplication exampleto start a communication between 1xPAC3200 and S7-1200. I have all the same equipement, but only PLC is different. It isS7-1200 CPU1212C AC/DC/RLY. After compiling program, I wanted to try my PAC. I used my adress of 40002 ( Va-n voltage) since i have no other measured size. Unfortunately I do not get any reading from the buffer. It is 0. If I disconect the pac from SWICH MODULE CSM1277, I get error so basically comunication exists. What could be the problem of not reading my data on MB_CLIENT. Best regards,
|
12/4/2013 5:27 PM | |
Joined: 7/7/2010 Last visit: 7/3/2024 Posts: 14899 Rating:
|
The address for 40002 in the PAC should simply be 2 when reading regular Modbus registers. perhaps a screenshot of your block configuration may help. |
science guy |
|
12/4/2013 9:48 PM | |
Posts: 6 Rating:
|
Yes, has been for a while now. You have either a Client or Server Block. The Client takes alittle more work of course but works well. |
12/5/2013 1:05 PM | |
Posts: 6 Rating:
|
It appears you at V12 SP1 UPD2, thats good. |