5/7/2021 2:02 PM | |
Joined: 4/14/2013 Last visit: 3/28/2024 Posts: 28 Rating: (1) |
Hello. About this.. 3 year ago, we have installed into asynchronous motor test centers 230V working controllers. Thus this are testing centers, short circuit in motor or inverter is a allowed condition. All power lines before motors or inverters are equipped with 3 phase reactor and power lines come through ferrite rings. Before motor fuses are 500mA Siemens RCCB-s. About protection the controller: Controller power lines come through main filters, ferrite rings and are bridged with varistors; same (varistors) is with comes inputs where a dangerous impulse can come from. (No UPS-es included on this project) Then.. 3 years of work and no problems found. So Vippi: only protection systems help avoid further problems, ferrites and varistors are a minimum program. |
This contribution was helpful to1 thankful Users |
5/27/2021 11:22 AM | |
Joined: 9/24/2008 Last visit: 3/11/2024 Posts: 106 Rating: (4) |
Here is one of the buffers I saved AttachmentDiagnostic_Buffer.txt (311 Downloads) |
Last edited by: Jen_Moderator at: 05/27/2021 13:04:56Added diagnostic buffer as txt. file. |
|
5/27/2021 1:27 PM | |
Joined: 9/24/2008 Last visit: 3/11/2024 Posts: 106 Rating: (4) |
I'm sorry but customer required CPU substitution after the problem because they feared it could be damaged. I have no access to the old one, I saved the buffer when the error occured. I thought the error code was enough to understand what happened.
AttachmentDiagnostic_Buffer_EN.txt (382 Downloads) |
Last edited by: Jen_Moderator at: 05/28/2021 06:47:44Added diagnostic buffer as txt. file. |
|