Input modules are powered by the backplane bus. so they get their power from the PS module. the U-connectors should indeed be connected to the PM. the PM can be positioned anywhere but you will have to manually wire it to the desired output modules, it does not power the backbus https://support.industry.siemens.com/cs/document/96998532/which-simatic-and-sitop-modules-can-you-use-with-s7-1500-as-load-power-supply-module-(pm)-?dti=0&pnid=13908&lc=en-US |