6/16/2010 12:39 PM | |
Posts: 8 Rating: (0) |
Dear Expert In the SM321- maximum cable length, shielded is 1000m & maximum cable legth, unshielded length is 600m. Please let me know the size of the cables. |
6/21/2010 9:51 AM | |
Joined: 5/28/2008 Last visit: 11/6/2024 Posts: 4516 Rating: (839)
|
Hello MBSYSTEMS, There will be no problem with 1mm or even 0.5mm specially there's no high current will follow through the wire I am sure. It looks that that DI is for an Emergency button or a limit switch. So the current that will follow through the cable is equal to few milli Amps. But I recommend to use a separite small power supply for this input and use a relay near the module to energize the input. Back to your last question. There will be no problem with 900 m You can use up to 600 m for un-shield cables & 1000 m for shielded cables. Please check the technical specification of your DI module. You will found it in Module data. |
Ayman Elotaify |
|
8/3/2015 3:39 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
|