Hello mhkocak,
Just to tell you, S7-400 has typically what you want. you canassignsome modules to a partition of process image which you assign to a cyclic interrupt organization block. This partition of process image gets refreshed synchronously with its OB. There's also SFC26 & SFC27 for refreshing process image when you need. Back to S7-300, You can manouvre with peripheral addressing to access modules directly. The point is, does it really worth the effort? S7-300 means to me an average scan cycle of15 to 30msec (By all means not exceeding 100msec). Do you have inputs that can change faster than your cycle time? I don't know what kind of inputs you have but if you have inputs with very fast change rates (High frequency) then there are some modules for that and if you have some inputs that may do harm if they are not caught in time, you can use hardware interrupt modules for them. Best regards. H-H |