6/26/2013 7:39 AM | |
Joined: 4/17/2012 Last visit: 3/30/2024 Posts: 474 Rating: (10) |
Hai, these are the basic blocks used for modbus tcp connection |
6/26/2013 7:47 AM | |
Joined: 4/17/2012 Last visit: 3/30/2024 Posts: 474 Rating: (10) |
Hi, Pls use the link to douwnload the file and zip folder then go ahead as per instruction , then it will full fill your requirement |
This contribution was helpful to1 thankful Users |
6/26/2013 1:35 PM | |
Joined: 9/27/2006 Last visit: 5/17/2024 Posts: 12257 Rating: (2668) |
Hello Naveen; I have not worked with this unit before, but I would expect you would have to establish Modbus/TCP as the protocol used, specify the Ethernet address and other parameters on the IND560 Since it would act as a server on the network, it cannot initiate communications (that is the privilege of the client, your PLC in this case) and you would have to read up on the Modbus mapping inside the IND560 so the client can read/write to the correct register addresses you need. Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
6/26/2013 3:43 PM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181)
|
Hello, I would suggest you to clarify with the seller what exactly interface card has been installed in IND560. Then as suggested above check in documentation CD.
Best regards, Hristo Mihalev
|
This contribution was helpful to1 thankful Users |