10/1/2012 9:34 PM | |
Joined: 10/24/2011 Last visit: 3/9/2023 Posts: 257 Rating: (1) |
Hello dchartier, I have checked configuration online and I didn't found any fault. As I mentioned I interchanged the modules for the same slot. The modules are same. Here are some images which have attched. Please go through it.
AttachmentImages.zip (77 Downloads) |
10/2/2012 3:35 AM | |
Hellodchartier, I found some of the modules configured as 4 wire [C] in hardware configuration and physically on module set as 2 wire [D]. Bur I'm not getting any fault on that module. Transmitters connected to channels of module are 2-wire. Does it cause modules or back connectors to malfunction? I'll check by changing hardware configuration today and will give you reply. Thanks, Shailesh