1/11/2021 1:39 PM | |
Posts: 114 Rating: (2) |
Hello All, I need to verify System architecture of S7-400H (6ES74125HK060AB0) SCADA -WINCC 7.5 SP1 (Both scada are standalone) Unmanaged Switch-(6GK50080BA101AB2) HMI-(6AV21240QC020AX1) 1) Is Unmanaged Switch is OK or Do I Required Managed Switch ? 2) USE OF CP 1623 ? Experts....!!!! Is there Anything I am Missing ???? Please Give Suggestion on Above SA. AttachmentR0.SA.pdf (373 Downloads) |
Last edited by: vicky bhau at: 01/11/2021 13:51:27 |
|
1/11/2021 2:03 PM | |
Joined: 2/2/2015 Last visit: 5/15/2024 Posts: 123 Rating: (21) |
Hi vicky, The unmanaged switch is enough for this application because you are not using mrp in the attached suggested topology. The use of CP 1623, is to configure the SCADA PC to the profinet network, although you can use the built-in ethernet port in the PC if you don't have the communication card. Regarding the IM module, will you use redundancy for it?? Read this topic Hope this is helpful, Regards; Ahmed |
Last edited by: Ahmed Kadry at: 01/11/2021 14:04:56 |
|
1/12/2021 7:38 AM | |
Posts: 114 Rating: (2) |
Hi Thanks for reply but if i will not use CP Card then How to Generate S7-Connection for communication with WINCC SCADA Thanks & Regards, Krushikesh |