2/17/2016 12:58 PM | |
Posts: 129 Rating: (17) |
Hi, Topic have been discussed previously... Check link below for the search results from the Forum Hope this helps, or post your CPU Details |
2/17/2016 6:46 PM | |
Posts: 2 Rating: (0) |
Thanks a lot for your reply , Please find below the vedio shows the problem |
2/17/2016 7:27 PM | |
Joined: 9/27/2006 Last visit: 7/14/2024 Posts: 12268 Rating: (2675)
Hello IAHMSA; In the following discussion there were a few very interesting posts describing your problem, with possible solutions.
flashing all LEDs on the CPU
https://support.industry.siemens.com/tf/ww/en/posts/27801/ Basically, all LEDs flashing means that the CPU is signalling a DEFECTIVE state. Here is how the Programming with Step 7 v5.5 manual suggest you react to a Defective state:
Defective, in other words, a fault has occurred.
To check whether the CPU is really defective, switch the CPU to STOP and turn the power switch off and then on again. If the CPU starts up, display the diagnostic buffer to analyze the problem. If the CPU does not start up it must be replaced.
Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 2/17/2016 7:31:12 PMLast edited by: dchartier at: 2/17/2016 7:32:30 PM |
1/9/2017 3:03 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4770 Rating: (123) |
New question published by Sald84 is split to a separate thread with the subject 416-3 DP goes to stop mode. Best regards |
3/24/2017 2:28 PM | |
New question published by okankse is split to a separate thread with the subject Open protected S7 400 simatic manager program. Best regards |