6/8/2009 11:03 PM | |
Posts: 196 Rating:
Hi amfirooz 1. Regarding witch hardware opration that can be done when the system is up can be found in this FAQ. http://support.automation.siemens.com/WW/view/en/22916606 2. For the download i can recomend this procedure in this tread /tf/WW/en/Posts/30620#top Hope this helps and remember to read the online Manuel for H-Systems. |
6/9/2009 5:45 AM | |
Posts: 272 Rating:
Hi Amifiroz, I think in H system we can do online download. As one of the CPU will go in stop mode and the other will take over as master. Rgrds, Prat |
6/16/2009 9:53 AM | |
Joined: 3/24/2009 Last visit: 7/9/2024 Posts: 535 Rating:
Dear amfirooz, ad 2) yes, it is correct, that you can download your program in the RUN-mode, but please check chapter 9.8.2.1 / 9.8.2.2 in this document: https://support.automation.siemens.com/WW/llisapi.dll/csfetch/2201072/step7_s7_f_fh_systems_programming_operating_manual_en-US.pdf?func=cslib.csFetch&nodeid=6359901&forcedownload=true If you have changes like those in chapter 9.8.2.2, you will not be able to activate the safety-mode after the download. Regards, yy1 |