hi SATYA SURAVIT, this should depend on the current they get from backplane-bus. This should be not higher than 1.2A. CP-modules normally have a higher current-consumption than other modules, so this would be the criterion for exclusion. See the technical data of the CP and the manual with this information:
S7-300 CPU 31xC and CPU 31x:Installation chapter 4.5
So you can totaly mount 6 CP343-1 modules on one rack hope this helps, regards, |