Joined: 9/27/2006 Last visit: 11/10/2024 Posts: 12293 Rating: (2691) |
Hello michael; You will need to look at an OPC connection between the PLC and the SCADA; the RSView 32 user manual suggests this type of connection: -on the SCADA side, install an OPC client: RSLinx Gateway -on the PLC side, setup an OPC server:
PUBLICATION VW32-UM001D-EN-E–August 2007Supersedes Publication VW32-UM001C-EN-E http://literature.rockwellautomation.com/idc/groups/literature/documents/um/vw32-um001_-en-e.pdf Hope this helps, Daniel Chartier |
||
6/23/2008 7:51 AM | |
Posts: 3 Rating: (0) |
Dear Daniel, Thank you for your quick response. I will try to set up and inform you ahead regarding the status. Best regards, mike |