2/17/2014 8:32 AM | |
Posts: 10 Rating: (0) |
nobody knows about it? i think it only happens to me. |
2/17/2014 11:52 AM | |
Joined: 8/25/2005 Last visit: 7/5/2024 Posts: 1161 Rating: (110) |
Hello muratb, my first thought was: Load a newer Firmware Version. But, ... think you allready got the newest available one Operating System Update for SIMATIC S7-1200 CPU Firmware V3 So I would suggest to contact the Technical Support via Support Request. Maybe they got a newer one? Please keep us up to date. Thank you Sabine |
2/17/2014 2:05 PM | |
Posts: 10 Rating: (0) |
firmware is up-to-date. i asked technical sport. they said it might be about harmonics. i am going to use UPS before cpu. an also i am going to change the cpu and wait. that s it...
|
This contribution was helpful to1 thankful Users |
3/14/2014 1:39 PM | |
Joined: 7/7/2010 Last visit: 9/26/2024 Posts: 15238 Rating: (2418)
|
If you use relay outputs, the inductive problem still exists but is less likely to affect the output module. Rather it will simply reduce the life of the output contacts. If you have a 24vdc coil on a plc output, you should add appropriate diode, and/or snubber. Maybe this link will help: http://electronics.stackexchange.com/questions/26140/inductive-kick-back-voltage-calculation |
science guy |
|
This contribution was helpful to1 thankful Users |