9/6/2012 7:25 PM | |
Posts: 947 Rating: (45) |
Hi, Manishkools EEPROM - This is flash card? I understand you correctly? |
9/18/2012 10:31 AM | |
in the slot of s7-400 PLC top side possible install also RAM card. What you need? |
9/19/2012 8:19 AM | |
Joined: 4/22/2010 Last visit: 11/15/2024 Posts: 5697 Rating: (715)
Hello, 1 battery + RAM After power return, PLC start normally from RAM and no DATA loss. 2 RAM + EEPROM After power return, PLC loads program from EEPROM into RAM, all DB are loaded with initial values. 3 ONLY RAM Program is lost and needs to be downloaded again. Regards, Marcjan Attachmentmemory card.pdf (516 Downloads) |
Last edited by: Marcjan at: 9/19/2012 8:29 AMattached part of manual Problem solved? |