Hi verbrennung, Is the problem resolved? Did you contact the tech support? Regards |
10/8/2012 10:34 PM | |
Joined: 1/15/2009 Last visit: 4/19/2024 Posts: 316 Rating: (40)
|
Hi ILM, verbrennung's process is correct, this is common for sites with SM 6.2 and PCS7 anything V7+, however one improvement that I advise users is to cut and paste the contents inside the GraCS folder somewhere else (desktop maybe?), leaving only the 20@PG_F_MATCTL* – @PG_F_MA_AL* – @PG_F_SC_AL* – @PG_F_SE_AL* – @PCS7Typicals_S7FSMTX.PDL faceplate files. With only those files in the GraCS folder, the convert will only take 2 minutes opposed to much longer for larger projects (seen it take 1.5 hrs). Then when the convert is complete, move the original contents back to the GraCS folder, and back to whereverbrennungdetailed on the ES. The reason for this is now the next project created on the ES, will be created with the correct file set of Safety Matrix faceplates. But at the end of this process, check the basic data tab again in OS Project Editor, there should no longer be the @pg_F_* faceplates......
|
The best location for all PCS 7 content (manuals, guides, application notes, FAQs, and videos). |
|
8/24/2016 10:26 AM | |
Posts: 567 Rating: (107) |
Hi, there are some requirements for operator control and monitoring. You can find them in the safety matrix manual chapter 8. One requirement is that there is no default server for tags is set on a OS Client. |