4/9/2016 12:25 AM | |
Joined: 9/27/2006 Last visit: 8/12/2024 Posts: 12276 Rating:
|
Hello Lucky; I do not consider myself an expert on the s7-1500 (yet!). However, I am still able to navigate the Siemens Support documentation.... SIMATIC Industrial Software SIMATIC Safety - Configuring and Programming https://support.industry.siemens.com/cs/ww/en/view/54110126 Scope of this documentation This documentation is valid for the optional packages STEP 7 Safety Advanced V13 SP1 and STEP 7 Safety Basic V13 SP1. ... Approvals The SIMATIC Safety F-system is certified for use in safety mode up to: ● Safety integrity level SIL3 in accordance with IEC 61508:2010 ● Performance Level (PL) e and category 4 in accordance with ISO 13849-1:2006 or EN ISO 13849-1:2008
...
Conventions
"(S7-1500)" indicates that the section only applies to S7-1500 F-CPUs. S7-1500 F-CPUs also includes ET 200SP F-CPUs. You might also appreciate the following Application Example:
Emergency stop up to SIL 3 / PL e with a fail-safe S7-1500 controller
https://support.industry.siemens.com/cs/ww/en/view/21064024 Hope this helps, Daniel Chartier
|
This contribution was helpful to
2 thankful Users |
4/9/2016 1:20 AM | |
Joined: 5/28/2008 Last visit: 8/6/2024 Posts: 4515 Rating:
|
Hello, Me too.. I don't consider my self an expert in S7-1500 But I can tell you according to technical specifications that Fail Safe CPU released are now SIL3 certified. For instance, have a look on the technical specification of 6ES7515-2FM01-0AB0 |
Ayman Elotaify |
|
This contribution was helpful to
3 thankful Users |
4/9/2016 6:48 PM | |
Joined: 5/28/2008 Last visit: 8/6/2024 Posts: 4515 Rating:
|
Hello, Just to add something, As I told to achieve SIL3 Redundancy in IOs is not a must. See this manual and go to Each module and see the flow chart which will guide you to achieve the needed SIL level For ET200M Fail Safe Modules SIMATIC Automation System S7-300 ET 200M Distributed I/O Device Fail-safe signal modulesFor ET200 MP (for S7-1500) there is no one manual for all modules, you have to download manual for each module. Foe example: For F-DI 16 Module: SIMATIC ET 200MP digital I/O module F-DI 16x24VDC |
Ayman Elotaify |
|
This contribution was helpful to
2 thankful Users |
4/10/2016 10:24 AM | |
Joined: 5/28/2008 Last visit: 8/6/2024 Posts: 4515 Rating:
|
Hello, I did not read this info but I have seen a video to compare the S7-300 & S7-1500 CPU performance. The comparison was based on measuring the scan cycle time, seeing the diagnosics on the S7-1500 display, ..etc You can see the video from here: Performance comparison CPU 1518-CPU 319Fore sure these are more features better in S7-1500 than those in S7-300 But also, desicion will still based on the application needs and price. |
Last edited by: Ayman Elotaify at: 4/10/2016 10:25:34 AMAyman Elotaify |
|
This contribution was helpful to
2 thankful Users |
Follow us on