11/14/2005 7:44 AM | |
Posts: 3149 Rating:
|
Hi Bog, well, I don´t think, that your idea to put all screens in a PDL is really usefull. => have a look at your C/VB-Scripts, I guess that you are using lots of them? http://support.automation.siemens.com/WW/view/en/10538600 http://support.automation.siemens.com/WW/view/en/12124767 http://support.automation.siemens.com/WW/view/en/10113139 http://support.automation.siemens.com/WW/view/de/22196555 Do you use GetTagxxxWait-/SetTagxxxWait-calls? http://support.automation.siemens.com/WW/view/en/18943009 You should first check your scripts with the WinCC-log files and APDiag. Good luck, Nemo |
11/14/2005 4:42 PM | |
Posts: 6 Rating:
|
Thanks |
10/30/2007 8:12 AM | ||
Posts: 2 Rating:
|
|
|
10/30/2007 9:36 AM | |
Posts: 2 Rating:
|
found a solution! Thanks to Nemo's link! http://support.automation.siemens.com/WW/view/en/10538600 just make an 'dummy' object in those screens that load slow and put some c-code in it (it doesn't have to be functional). the importent part is to add all the tags that you ar using in scripts to the tag trigger section. see explenation on nemo's link. Problem solved! Thanks PeejeeP |
Last edited by: PeejeeP at: 30.10.2007 09:37 |
|